Member
I still do not have a clear understanding of the following hypothetical situation. One of the existing electrical system grounding electrodes is a ground ring. This ground ring satisfies all the NEC requirements. We decided to install a brand new LPS. This LPS has five down conductors. I realize that the electrical system ground ring also satisfies all the rules of the NFPA 780 for a ground ring. I consider, then, in lieu of installing dedicated LPS grounding electrodes, to use the existing electrical system ground ring. Then I read that the NFPA 780 says, "Electrical system grounding electrodes shall not be used in lieu of lightning protection system grounding". This seems to be a problem because instead of installing dedicated LPS grounding electrodes, I am using an existing electrical system grounding electrode in direct violation of NFPA 780. Any thoughts?