Is it acceptable to remove the insulated conductors from NM and use them in conduit (where one would normally use THHN/THWN or XHHW) ?
Is it acceptable to remove the insulated conductors from NM and use them in conduit (where one would normally use THHN/THWN or XHHW) ?
Sort of nit -picky, but IMO it's not just that they are not marked, it's that they are not an NEC conductor. If you look at the standards for NM, there is a whole bunch of messy language that doesn't really say the inners are thhn.
They are an NEC recognized conductor. See 334.112.
It's just they're not required to be marked individually.
I have *very* rarely seen marked conductors inside actual Romex branded NM-B, but not in years, perhaps before General Cable was bought by Southwire. I recall reading from an unverifiable source (more forum chatter) that marked conductors would occasionally be used in NM if the factory had run low/out of unmarked thhn, implying that it was simply an expedient and not a specification. But again, that part is all just innuendo.
But whether they're marked or not, they're required to be an NEC-recognized conductor/insulation.
Tough pull.You can use the conduit as a sleeve for NM though.
No, UF in PVC is a tough pull. :roll:Tough pull.
They are an NEC recognized conductor. See 334.112.
It's just they're not required to be marked individually.
334.112 Insulation. The insulated power conductors shall
be one of the types listed in Table 310.13(A) that are suitable
for branch-circuit wiring or one that is identified for
use in these cables.
This?
334.112 Insulation. The insulated power conductors shall
be one of the types listed in Table 310.13(A) that are suitable
for branch-circuit wiring or one that is identified for
use in these cables.