art
Member
- Location
- California
- Occupation
- Electrical Engineer
We have 450' of conduit feeding a load and using the conduit as the ECG. trying to install a ground wire and can not get the wire through the last 150'. We measured the resistance of the entire path and got about 30 ohms. will this be enough to trip the breaker? And, does the resistance have to be 25 ohms anyway? If I divide 240 V by 30 ohms I get 8 Amps which will not work but I'm not sure is this is the right approach.
also, how do I compare if we use the wire ECG?
also, how do I compare if we use the wire ECG?