- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Please see attached sketch. I have 480/277V three phase coming into switchboard with 4 service disconnects. One of the service disco feeds trough thru FDR #1. Trough their is a tap one feeder FDR #2 goes to tenant 1 meter by utility and another feeder FDR #3 goes to tenant 2 meter by utility. From meter FDR#4 and FDR#5 go to each respective tenants.
Conduits are used as equipment grounding conductor (EGC). FDR #1 utilize two locknuts one inside other outside SWBD and wire trough. FDR #2 ,#3 utilize two locknuts one inside and one outside wire trough and Meter. FDR #4,#5 utilize 2 locknuts on meter side and Grounding bushing on tenant disconnect side.
Question this is not line side of service disconnect but it’s load side and utility meters are load side. In such situation would above mention method of using metal conduit as EGC bonding be per code? If not then what should it be?
Conduits are used as equipment grounding conductor (EGC). FDR #1 utilize two locknuts one inside other outside SWBD and wire trough. FDR #2 ,#3 utilize two locknuts one inside and one outside wire trough and Meter. FDR #4,#5 utilize 2 locknuts on meter side and Grounding bushing on tenant disconnect side.