Hello all,
I have a memory of a conversation I had with an engineer that trained me years ago about using a transformer's primary-side equipment grounding conductor as the separately derived system's grounding electrode conductor as long as the conductor was sized appropriately.
Example: assume you have a 480-208V 75 kVA transformer fed from a 125A breaker. Assume secondary conductors are 300 kcmil copper. In this case, the transformer's EGC is required to be 6 AWG copper per 250.122. The GEC is required to be 2 AWG copper per 250.66. The system bonding jumper is in the transformer enclosure. Assume further that the panel feeding the transformer (containing the 125A breaker) is bonded to the grounding electrode system with a 2 AWG GEC.
In the above scenario, is it allowable to install a 2 AWG grounding conductor between the source panel and the transformer that serves both as the transformer's EGC and as the separately derived system's GEC?
Unless my memory is faulty (and it very well may be), my supervising engineer told me years ago that this was common practice in some institutions in order to avoid many multiple GEC's throughout the building, and I even think we found the code section where it was specifically allowed.
However, I cannot find in the 2020 NEC where such an installation is allowed.
I appreciate anyone's input on this.
Thank you.
I have a memory of a conversation I had with an engineer that trained me years ago about using a transformer's primary-side equipment grounding conductor as the separately derived system's grounding electrode conductor as long as the conductor was sized appropriately.
Example: assume you have a 480-208V 75 kVA transformer fed from a 125A breaker. Assume secondary conductors are 300 kcmil copper. In this case, the transformer's EGC is required to be 6 AWG copper per 250.122. The GEC is required to be 2 AWG copper per 250.66. The system bonding jumper is in the transformer enclosure. Assume further that the panel feeding the transformer (containing the 125A breaker) is bonded to the grounding electrode system with a 2 AWG GEC.
In the above scenario, is it allowable to install a 2 AWG grounding conductor between the source panel and the transformer that serves both as the transformer's EGC and as the separately derived system's GEC?
Unless my memory is faulty (and it very well may be), my supervising engineer told me years ago that this was common practice in some institutions in order to avoid many multiple GEC's throughout the building, and I even think we found the code section where it was specifically allowed.
However, I cannot find in the 2020 NEC where such an installation is allowed.
I appreciate anyone's input on this.
Thank you.