I have a question about using ground bars (NEC 2011). I was asked if a large common ground bar could be placed next to a bldg's service disconnect for convenience of bonding ALL electrodes at a single point, including the grounding electrode conductor from the service equipment.
(See horrible graphic at bottom of post for a "visual" of what I am trying to explain.)
I think this would violate 250.64(C), but I have seen it often enough to make me wonder if I am missing something. Can somebody please clarify?
Also, this is for a main service to a building, indoor 1600A, 480V, Service equipment. It is not for a separately derived system.
<-------- [ground Rods] <-------- [Ground Bar] <-------- [Neutral Bus in Main Service Disc.]
<-------- [Water Main]
<-------- [Bldg Steel]
<-------- [Etc. ]