00crashtest
Senior Member
- Location
- California
- Occupation
- electrician trainee
I was reading Electrical Wiring Commercial 17th Edition, which is based on the 2020 National Electrical Code, and page 284 said,
However, I could not find any code references prohibiting it. I searched online and could only find on forums that one could not use it because they would not be able to find a single-pole breaker rated 208 volts and that the voltage would be unstable from unbalancing the three-phase high-leg delta transformer.
The reason why a high-leg to neutral single-phase circuit would be useful is precisely because it provides 208 volts between conductors, and Japanese split-phase appliances use 200 volts without also requiring 100 volts for the controls (unlike how split-phase appliances in North America require 120 V for the controls in addition to 240 V for the heating loads). The voltage imbalance on the transformer can be mitigated by having only a small fraction of loads be high-leg to neutral, because one wouldn't typically be using Japanese appliances in North America anyways.
However, a lodging facility popular with tourists from Japan or a community in North America with a high concentration of people who frequently travel between Japan and North America would benefit greatly from having 208 V power outlets to power their 200 V small kitchen appliances as intended by the manufacturer, especially if the equipment is bought in Japan west of the Fuji River, including the Kansai Region for Osaka, where the grid also runs on 60 Hz. This is especially useful because small kitchen appliances involving heating can easily fit within checked baggage. This is also especially helped by the fact that Japanese 200 V 15 A and 200 20 A plugs can be plugged into NEMA 6-15 and 6-20 receptacles respectively. Anyway, most appliances are typically rated for both 50 and 60 Hz in order to also be sold in the largest metropolitan area, which is the Kanto Region for the city of Tokyo, where they use 50 Hz. Granted, I see on travel and expatriate forums that most 200 V appliances from Japan work just fine on both 220 V 50 Hz European and 240 V 60 Hz North American as long as they are not on the highest setting. However, one would want their appliance to work as design intended on all settings.
In Article 210 for branch circuits, I could only find section 210.21 for Outlet Devices stating,
In Article 240 for overcurrent protection, I could only find section 240.83 for Marking stating,
So, can't one just use supply NEMA 6-20 receptacle(s) (which also accept NEMA 6-15 plugs and consequently both 200 V 15 A and 200 V 20 A JIS plugs) on a branch circuit that is 208 volts from high-leg to neutral (making it not a multi-wire branch circuit in this case) and is rated 20 A using a single-pole breaker rated for 20 A at 277 volts (or also 347 volts for Canada, the Pacific Northwest, and the US South) as long as they keep the branch circuit load under a relatively small proportion, such as 25% of the service transformer current rating?
The voltage between “B” and “N” is 208 volts. The “B” phase is called the high leg and cannot be used for lighting or other line-to-neutral purposes.
However, I could not find any code references prohibiting it. I searched online and could only find on forums that one could not use it because they would not be able to find a single-pole breaker rated 208 volts and that the voltage would be unstable from unbalancing the three-phase high-leg delta transformer.
The reason why a high-leg to neutral single-phase circuit would be useful is precisely because it provides 208 volts between conductors, and Japanese split-phase appliances use 200 volts without also requiring 100 volts for the controls (unlike how split-phase appliances in North America require 120 V for the controls in addition to 240 V for the heating loads). The voltage imbalance on the transformer can be mitigated by having only a small fraction of loads be high-leg to neutral, because one wouldn't typically be using Japanese appliances in North America anyways.
However, a lodging facility popular with tourists from Japan or a community in North America with a high concentration of people who frequently travel between Japan and North America would benefit greatly from having 208 V power outlets to power their 200 V small kitchen appliances as intended by the manufacturer, especially if the equipment is bought in Japan west of the Fuji River, including the Kansai Region for Osaka, where the grid also runs on 60 Hz. This is especially useful because small kitchen appliances involving heating can easily fit within checked baggage. This is also especially helped by the fact that Japanese 200 V 15 A and 200 20 A plugs can be plugged into NEMA 6-15 and 6-20 receptacles respectively. Anyway, most appliances are typically rated for both 50 and 60 Hz in order to also be sold in the largest metropolitan area, which is the Kanto Region for the city of Tokyo, where they use 50 Hz. Granted, I see on travel and expatriate forums that most 200 V appliances from Japan work just fine on both 220 V 50 Hz European and 240 V 60 Hz North American as long as they are not on the highest setting. However, one would want their appliance to work as design intended on all settings.
In Article 210 for branch circuits, I could only find section 210.21 for Outlet Devices stating,
and(B)(1) Single Receptacle on an Individual Branch Circuit. A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit.
(B)(3) Receptacle Ratings. Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21(B)(3), or, where rated higher than 50 amperes, the receptacle rating shall not be less than the branch-circuit rating.
In Article 240 for overcurrent protection, I could only find section 240.83 for Marking stating,
(E) Voltage Marking. Circuit breakers shall be marked with a voltage rating not less than the nominal system voltage that is indicative of their capability to interrupt fault currents between phases or phase to ground.
So, can't one just use supply NEMA 6-20 receptacle(s) (which also accept NEMA 6-15 plugs and consequently both 200 V 15 A and 200 V 20 A JIS plugs) on a branch circuit that is 208 volts from high-leg to neutral (making it not a multi-wire branch circuit in this case) and is rated 20 A using a single-pole breaker rated for 20 A at 277 volts (or also 347 volts for Canada, the Pacific Northwest, and the US South) as long as they keep the branch circuit load under a relatively small proportion, such as 25% of the service transformer current rating?