If you have a unit like KWh, and I know I may be asking the obvious here, but don’t you then just multiply that by the hours of use to get your need? If continuous for 24 hours don’t you just multiply by 24? Or is it just too easy and we use another formula??
I mean, it is holiday and formula one time... not too much thinking right now..
Only if you know that the net kWhr recorded was at a continuous kw during the duration the reading was taken.
If measurement was 10 kWhr in 24 hours, it could have been steady 416 watts for 24 hours, or it could have been 9 kWhr in 10 hours at a steady rate and remainder varied over the next 14 hours, or all sorts of combinations. for the purpose of what OP is trying to do though, one needs to know the peak demand in order to properly select conductors, switchgear, transformers, etc. that must be able to carry that peak demand when it is called for.
If you are bailing water out of a vessel one bucket at a time and it takes a million buckets to completely empty it, you use same energy to empty it, but if you do it ten buckets a minute vs 1000 buckets a minute it will be at different energy rates and of course the same work is completed but in different time as well. Calories consumed per minute is also going to vary greatly, even though same work was accomplished, this all assumes you don't tire out and can maintain steady work output at either rate.