Using lugs for termination

TMMB

Senior Member
Location
EGYPT
Occupation
Electrical Manager
Is it mandatory to use lugs for termination of building wires in circuit breakers or can directly connect wire to the circuit breaker
 
All breakers listed to UL 489 have terminations suitable for Class B and C stranded conductors for breakers over 30 amps and breakers 30 amps or less have termination suitable for solid, Class B and Class C stranded conductors.

The conductors in this thread are not of a type permitted by the NEC, and do not know what the stranding may be.
 