Using Meter Mains As Disconnect device

Status
Not open for further replies.

FaradayFF

Senior Member
Location
California
Hello,

Can meter mains serve as service entrance disconnect switch for distribution XFMR if located immediately on the secondary of the XFMR? I have a distribution XFMR that has service meter with integral circuit breaker connected directly on its secondary side. Per NEC, I need to have a disconnect. was wondering if this setup would be acceptable if all I have on the primary side is pole mounted fuse cut outs of the said XFMR.

Any suggestions would be appreciated.
Thanks,
EE
 

nhee2

Senior Member
Location
NH
Hello,

Can meter mains serve as service entrance disconnect switch for distribution XFMR if located immediately on the secondary of the XFMR? I have a distribution XFMR that has service meter with integral circuit breaker connected directly on its secondary side. Per NEC, I need to have a disconnect. was wondering if this setup would be acceptable if all I have on the primary side is pole mounted fuse cut outs of the said XFMR.

Any suggestions would be appreciated.
Thanks,
EE

Is the transformer a utility-transformer? If yes, then yes the main CB can be your service disconnect.
 