Can a concentric neutral that is part of an MV cable shield be used to satisfy the equipment grounding conductor (EGC) requirement per NEC 250.122?
For example can a cable with a 1/3 rated concentric neutral be used as an EGC if the current carrying capacity meets the requirement of table 250.122? I believe in this case the upstream overcurrent device rating used for 250.122 would be the CT ratio or ground fault pickup setting of relay?
Can the concentric neutrals of all (3) cables be added to account for EGC size or only one at a time can be considered?
I know the NEC allows use of a tape shield as an EGC as long as it rated to carry fault current based on fault clearing time (typically not applicable on solidly grounded systems) so I was wondering if with a concentric neutral the current carrying capacity of concentric neutral gets applied directly against 250.122 based on CT ratio or GF pickup or if relay clearing time for faults must also be considered?
For example can a cable with a 1/3 rated concentric neutral be used as an EGC if the current carrying capacity meets the requirement of table 250.122? I believe in this case the upstream overcurrent device rating used for 250.122 would be the CT ratio or ground fault pickup setting of relay?
Can the concentric neutrals of all (3) cables be added to account for EGC size or only one at a time can be considered?
I know the NEC allows use of a tape shield as an EGC as long as it rated to carry fault current based on fault clearing time (typically not applicable on solidly grounded systems) so I was wondering if with a concentric neutral the current carrying capacity of concentric neutral gets applied directly against 250.122 based on CT ratio or GF pickup or if relay clearing time for faults must also be considered?