Member
My inspector has brought up an issue this morning.
He pointed to Hoffman's UL sticker. "Enclosure openings must be filled by equipment with the same Type rating as the enclosure."
We used a N3R hinged door for 80 some odd locations. When indoors we used compression connectors and not rain tight connectors that we used outdoors. His statement was that this violated the UL listing of the Haffman enclosure.
Huh?
As I wait for a clarification from Hoffman, my only response is....are you kidding?
Can anyone validate or invalidate this?