Dsg319
Senior Member
- Location
- West Virginia
- Occupation
- Wv Master “lectrician”
Can one use an ohm meter between say feeder neutral and EGC bonded to case to be able to calculate and do simple math (ohms law) in the event of a fault to the case. Example feeder neutral resistance to bonded EGC to case on disconnect, protected with 400amp fuse at service hundreds of feet away.
120v/1ohm=120amps (not capable of clearing the fault with a 400amp fuse)
I know fault current calculations are much more detailed and take a lot more into account. Was just curious if one could use simple dc resistance from an ohm meter reading do this.
120v/1ohm=120amps (not capable of clearing the fault with a 400amp fuse)
I know fault current calculations are much more detailed and take a lot more into account. Was just curious if one could use simple dc resistance from an ohm meter reading do this.