Using Romex in commercial applications?

Status
Not open for further replies.

Aledrell

Senior Member
I know some of you out there will shutter at the thought and perhaps give me a hard time, but I want to be sure that the code is as I remember. That Romex can be used in a commercial buildings less than 3 stories and wood framed? What about boxes? Must you still use metal cutins or is plastic ok? There is no drop ceiling, but the little bit of existing wiring was done in mc or bx. Thx for any advice.
 
I know some of you out there will shutter at the thought and perhaps give me a hard time, but I want to be sure that the code is as I remember. That Romex can be used in a commercial buildings less than 3 stories and wood framed? What about boxes? Must you still use metal cutins or is plastic ok? There is no drop ceiling, but the little bit of existing wiring was done in mc or bx. Thx for any advice.

The three story limitation has been gone for a while but now it is against the code to use NM above a suspended ceiling in a non-dwelling unit.
 
The prohibition is based on the building type not the number of stories. The type is determined by the building code.

334.10(3) Other structures permitted to be of Types III, IV, and V
construction except as prohibited in 334.12. Cables
shall be concealed within walls, floors, or ceilings that
provide a thermal barrier of material that has at least a
15-minute finish rating as identified in listings of fire-
rated assemblies.
Informational Note No. 1: Types of building construction
and occupancy classifications are defined in NFPA 220-
2009, Standard on Types of Building Construction, or the
applicable building code, or both.
Informational Note No. 2:
See Informative Annex E for
determination of building types [NFPA 220, Table 3-1].
 
The three story limitation has been gone for a while but now it is against the code to use NM above a suspended ceiling in a non-dwelling unit.

There is no suspended ceiling in this building, it's all hard lid wood framed from what I have seen. The task at hand is adding 4 outlets to a 30 ft wall that has only one existing. Using the existing outlet circuit.
 
Last edited:
You (or an Architect, Engineer, or Building Code Official) need to determine the building type based on the building code. Take a look at Annex E for some information in the NEC.
 
And the best place to start for information is usually the life safety plan page or the "Building summary" informationt that should be on most sets of plans.
 
And the best place to start for information is usually the life safety plan page or the "Building summary" informationt that should be on most sets of plans.

Agreed. Here, there are quite a few commercial environments that we can use romex in, just not in a drop ceiling.

Anyone know the reason we cant run romex in a commercial drop ceiling, but in a home drop ceiling, its fine?
 
You (or an Architect, Engineer, or Building Code Official) need to determine the building type based on the building code. Take a look at Annex E for some information in the NEC.

According to Ryan Jackson, resident expert on the IBC (;)), Annex E is worth it's weight in toilet paper. The OP should probably refer to the original drawings of the job or consult the AHJ / building code.
 
Agreed. Here, there are quite a few commercial environments that we can use romex in, just not in a drop ceiling.

Anyone know the reason we cant run romex in a commercial drop ceiling, but in a home drop ceiling, its fine?

Politics relating to steel conduit manufacturers, I believe.
 
According to Ryan Jackson, resident expert on the IBC (;)), Annex E is worth it's weight in toilet paper. The OP should probably refer to the original drawings of the job or consult the AHJ / building code.

This building was built in the 50's, and as under went a few additions over the years. There are no plans to speak of for this job, it's simply a commercial tenant wanting a few more outlets on a wall. Customer is cost conscious and thought since it was all wood framing and absolutely no drop ceiling anywhere, that Romex could be used. I ended up using Romex but used metal cut-ins. I was just concerned that maintainance guy for the building might complain if he saw Romex, but if I'm within the letter of the code I don't care what he thinks.
 
Right, but they could have repealed it wholesale. I think a limitation of any kind is a tip of the hat to the steel manufacturers, akin to the nonsensical exceptions to 210.12.
 