D dhsvcs Member Location miami Occupation electrician Mar 14, 2024 #1 are there any occasions when romex/nmb can be used in a large multi-story ( 20 story bldg ) condo unit ?
are there any occasions when romex/nmb can be used in a large multi-story ( 20 story bldg ) condo unit ?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Mar 14, 2024 #2 See 334.10(5). (5) Types I and II construction where installed within raceways permitted to be installed in Types I and II construction. Click to expand...
See 334.10(5). (5) Types I and II construction where installed within raceways permitted to be installed in Types I and II construction. Click to expand...
Johnhall30 Senior Member Location New Orleans, LA Occupation Engineer Mar 14, 2024 #3 Look over article 334 as a whole, and it should answer your question on where NM can and can't be used
Look over article 334 as a whole, and it should answer your question on where NM can and can't be used