On another forum a photograph was posted of a panel with the cover removed. All of the Type NM cables entered a 2 inch nipple for the short jump to the attic above. The photograph did not show the other end of the EMT but several contributors stated that it is quite common to use a short nipple that way with only a bushing at the upper end. Leaving out the conduit being stuffed way beyond the 60% permitted by note 4 of the Notes to tables in chapter 9 with no visible space between the cable jackets which were stripped back to the end of the EMT connector is it not an NEC violation for these cables to just exit the bushing at the upper end of the nipple to be supported by the usual staples, clips, or bored holes? Lets even say that they are supported withing the 9 inches as would be required for a box without clamps. It just sounds wrong to me. So leaving the fill issue alone is it really code compliant to use a <24 inch long EMT nipple to carry any number of cables that you can squeeze into 60% of the cross section to a point up to 2 feet away from the panel cabinet and then support them just like you would with Type NM cable at a box with no clamps?