Using Solid Green colored wire
EEC
Maryland
Can solid green colored wire be used for the fan on connection to thermostat 24 volts. What article of NEC code is answer based on?
I'm slightly confused, is the wire for the fan? or for the thermostat?
if fan: no
if thermostat wiring : It could be ok depending on wire type
250.119 read all - note Exception, I doult you'll make that exception.
In the Article 100 read Grounded, Solidly or determine if its a Grounding Conductor, Equipment (EGC)
He should meet the exception. When I was working with the tools the green thermostat wire was the usually hooked up to the fan circuit. That qualifies as a class 2 circuit.
Agreed, T-stat wiring is one of the things that prompted the addition of the exception to 250.119.
Chris