Using table 220.44

Status
Not open for further replies.

morg123452000

Member
Location
maine usa
In doing a calculation on a non dwelling for my 120 volt receptacles..and I have determined it is a continous load..computors.is one example do I add those to the general purpose receptacals I've noticed some caculations dont...they are figured separate with lights and other continous loads
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I believe this would fall under 220.14(A)

(A) Specific Appliances or Loads. An outlet for a specific
appliance or other load not covered in 220.14(B) through
(L) shall be calculated based on the ampere rating of the
appliance or load served.
 