My company is one of several companies doing engineering a large (310 loads) water plant (greenfield). The loads are basically pumps pumping water solutions and HVAC type fans. The motors are IEEE-841 version Design B. The chief "Engineer" for the project is insisting on using a technique to size the (time-delay AJT type) fuses for the low voltage motors that I am not comfortable with. Table 430.52 in the NEC gives a limit of 175% of FLA for the maximum fuse size for time-delay dual element. Exception #1 allows you to jump to the next standard fuse size when the 175% doesn't match a standard fuse size. Exception #2(b) allows you to jump to the next standard size, not exceeding 225% of FLA when the 175% fuse or the fuse permitted in Exception 1 is "not sufficient for the starting current of the motor". The clients chief Engineer is citing a paper by Mersen and saying that we can go ahead and jump to the 225% without trying the start the motors with the smaller fuse. My question is can you use an engineering paper like this to determine that the 175% fuse is "not sufficient for the starting current of the motor"?
Here is the link to the Mersen paper: http://ep-us.mersen.com/fileadmin/c...on-Low-Voltage-Fuses-For-Motor-Protection.pdf
See the Table on P12 and the note underneath the table for "Heavy Load".
Actually the facility is in Canada and would be under the CSA. However, I can't find a good forum on the CSA and I would be interested in hearing how this issue would be approached using the NEC. The rules in the CSA seem very similar if not identical to the NEC on this.
I was considering insisting that they have the AHJ "buy in" on this but didn't know if I was being to "hard line"?
Here is the link to the Mersen paper: http://ep-us.mersen.com/fileadmin/c...on-Low-Voltage-Fuses-For-Motor-Protection.pdf
See the Table on P12 and the note underneath the table for "Heavy Load".
Actually the facility is in Canada and would be under the CSA. However, I can't find a good forum on the CSA and I would be interested in hearing how this issue would be approached using the NEC. The rules in the CSA seem very similar if not identical to the NEC on this.
I was considering insisting that they have the AHJ "buy in" on this but didn't know if I was being to "hard line"?