Using the optional calculation method, what is the calculated load for a service serving a single family dwelling when given the following information.
The dwelling has 1200 Sq. Ft. and the following electrical appliances that are fastened in place!
1-240 Volt 10 KVA range
1-240 volt 4800 Va clothes dryer
1-disposal 750 VA
The air conditioning is rated at 5000 VA and the baseboard heating, which is controlled by six separate thermostats is rated at 10000 VA.
I have followed my study manual and got. 19740 VA
The answer provided is 20460 VA.
I have worked this several times and I am not getting the same answer as the one provided. It is really making me second guess all I have learned regarding residential load calculations.