The code requires the water service to be used as a grounding electrode for the electric service when available.
What happens when the water service is a really far away from the electric service? Is it required to run a ground wire clear across the building? Or can the water service be connected to the building steel, and then connect the steel to the service ground?
And does the wire have to be sized per table 250.66? It doesn't look like there is a exception for a water pipe like there is for rod, pipe, and plate electrodes that reduces the wire size to a #6.
What happens when the water service is a really far away from the electric service? Is it required to run a ground wire clear across the building? Or can the water service be connected to the building steel, and then connect the steel to the service ground?
And does the wire have to be sized per table 250.66? It doesn't look like there is a exception for a water pipe like there is for rod, pipe, and plate electrodes that reduces the wire size to a #6.