When selecting a THHN wire based on 90 degree insulation but terminating onto a 75 degree Cel rated device you must not select an ampacity higher than that for a 75 degree rated wire.
But can you select a THHN with an ampacity just under 75 degree ampacity?, I assume this depends on load ampere demand? Such as lights needing 12 amps and THHN selected after adjustment and temp correction yields 8 amperes?
But if your load requires 20 amperes and you select a THHN rated 90 a 14 AWG which allows 25 amperes before hurting insulation then since your load only uses 20 amperes which is what the 75 degree rated wire will allow and not only will the breaker be sized for 20 Amperes but the THHN wire will only see 20 amperes (temp limit of 20 amperes) then why couldn’t you use this?
All sources seem to say THHN must be limited to an ampacity of 20 which is the 75 degree column conductor. However it’s the load and somewhat breaker which determines the amperes going through a wire but not wire nor insulation itself.
This still isn’t making sense
But can you select a THHN with an ampacity just under 75 degree ampacity?, I assume this depends on load ampere demand? Such as lights needing 12 amps and THHN selected after adjustment and temp correction yields 8 amperes?
But if your load requires 20 amperes and you select a THHN rated 90 a 14 AWG which allows 25 amperes before hurting insulation then since your load only uses 20 amperes which is what the 75 degree rated wire will allow and not only will the breaker be sized for 20 Amperes but the THHN wire will only see 20 amperes (temp limit of 20 amperes) then why couldn’t you use this?
All sources seem to say THHN must be limited to an ampacity of 20 which is the 75 degree column conductor. However it’s the load and somewhat breaker which determines the amperes going through a wire but not wire nor insulation itself.
This still isn’t making sense