Using two breakers as one.

Status
Not open for further replies.

cooltc2004

Member
Location
Ohio
If I have 2 FAX C50/2 in a panel and want to know if I use a busbar to connect 1-3 and 2-4 (in a single phase configuration) and use the appropriate sized wire, if I can pull 80A out of the two connections?

I know I can feed the breakers this way if needed, but I'm not familiar if I can feed the components out of the breaker this way.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
The NEC does not allow circuit breaker poles to be paralleled except in a listed manufactured assembly, as is found in some main breakers.

Sent from my XT1585 using Tapatalk
 
  • Like
Reactions: Zee

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
To add the article section to GoldDigger's post see 240.8

Roger
 

cooltc2004

Member
Location
Ohio
Thank you guys for the response. That NEC reference is exactly what I was looking for.

does this go for feeding the breakers as well?
 

kwired

Electron manager
Location
NE Nebraska
Thank you guys for the response. That NEC reference is exactly what I was looking for.

does this go for feeding the breakers as well?
If you are asking if you can feed them with paralleled conductors, the answer is yes, but with some rules. First one for a breaker of that rating is that the terminations will likely only be rated for a single conductor, which means you will need some method to adapt more then one conductor into the single conductor that connects to the breaker.

Second issue also typically that makes this impractical on a breaker the size you are dealing with is that paralleled conductors must usually be 1/0 AWG or larger.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
If you are asking if you can feed them with paralleled conductors, the answer is yes, but with some rules. First one for a breaker of that rating is that the terminations will likely only be rated for a single conductor, which means you will need some method to adapt more then one conductor into the single conductor that connects to the breaker.

Second issue also typically that makes this impractical on a breaker the size you are dealing with is that paralleled conductors must usually be 1/0 AWG or larger.

Instead of posting solely for post count it would be a good idea to actually read the questions and or title of the thread "Using two breakers as one."

Roger
 

kwired

Electron manager
Location
NE Nebraska
Instead of posting solely for post count it would be a good idea to actually read the questions and or title of the thread "Using two breakers as one."

Roger
I was replying to this:

does this go for feeding the breakers as well?

I don't know what that is asking, we already clarified and OP seemed to understand that you can't parallel the breakers themselves before that was asked. "Feeding the breakers" about has to apply to supply conductors.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Side note:
Manufacturers do this all the time, especially for main breakers in low cost load centers, so people see that and ASSume they can replicate it in the field. That's not the case. When a breaker mfr has done this, the pairs are specially designed, calibrated, tested and listed as a single breaker.
 
  • Like
Reactions: Zee

JFletcher

Senior Member
Location
Williamsburg, VA
Some equipment, like high kW on-demand/instantaneous water heaters, may have up to 3 sets of breakers feeding them, but they would have, say, 3 2p 60A breakers with #6 wire feeding what's essentially 3 heaters in one unit. You could not use 6 2p 30A breakers and/or doubled up #10 wire to feed such a unit.

What is "FAX C50/2"? A Google search came up blanks.

Paralleling breakers is not done, because, among other reasons, it's impossible to have even amperage across the two. Paralleling wire is only done in larger sizes and with strict guidelines (wires are same construction, size, type, length, run the same way/path, same raceway, etc.).
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Side note:
Manufacturers do this all the time, especially for main breakers in low cost load centers, so people see that and ASSume they can replicate it in the field. That's not the case. When a breaker mfr has done this, the pairs are specially designed, calibrated, tested and listed as a single breaker.

I have never noticed a parallel circuit breaker. Maybe it's there and I just didn't notice because it only had one handle.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I have never noticed a parallel circuit breaker. Maybe it's there and I just didn't notice because it only had one handle.
Bob,
You and I deal mostly with industrial stuff, it's never used there, only in low cost residential load centers starting maybe 15 years ago or so. I had never seen it either until I went to work for Siemens and the first time I saw it I thought is was a user adaptation, telling the guy asking for it that it was bogus. I was wrong...
 
  • Like
Reactions: Zee