I have a situation where we ended up not using a 480V 1.5HP in line fan and it's ABB VFD during construction of one of our buildings. Now I am going to donate the fan and drive to a good friend who is remodeling a local tavern he just purchased, issue is he only has 240V single phase power available (this will be kicked up to 480V 1Ph). I don't run into situations where I am using freak drives to run a 3 phase load from a single phase source, and that is where my question lies.
I know normally in this situation, you would double the size of the drive to handle the extra power needed to run the fan. The plan is to install differential pressure sensors in the smoking room and one in the bar area. We'll then be exhausting enough to meet minimum ventilation needed to keep the room smoke free plus keeping the room negative so the smoking room doesn't draft into the bar area. Mostly the fan will be running at minimum levels but may have times especially when doors open where it needs to ramp up to keep the negative state. Seeing as it will 95% of the time be running at far less than 50% of it's full load, any opinions on if the drive will work and if not how long it'll last?
Thank You
I know normally in this situation, you would double the size of the drive to handle the extra power needed to run the fan. The plan is to install differential pressure sensors in the smoking room and one in the bar area. We'll then be exhausting enough to meet minimum ventilation needed to keep the room smoke free plus keeping the room negative so the smoking room doesn't draft into the bar area. Mostly the fan will be running at minimum levels but may have times especially when doors open where it needs to ramp up to keep the negative state. Seeing as it will 95% of the time be running at far less than 50% of it's full load, any opinions on if the drive will work and if not how long it'll last?
Thank You