Presumably this is split phase, so the neutrals do not count as a CCC. This you have 4 CCC requiring an 80% adjustment. You must use the 75 temp ampacity due to terminal limitations, but can derate from the 90 degree. It works out using the next size up rule as you have shown as long as you use the 250 MCM, the 4/0 is too small.

Not sure if a 2 1/2 LB is sufficient. You would have to see what it is marked with and of course it won't have the combination of conductors you have. I think there is a letter from an lb manufacturer floating out there that says for combinations not printed on the lb you can compute the area of your conductors and as long as it is the same or less you're okay.
 
Presumably this is split phase, so the neutrals do not count as a CCC. This you have 4 CCC requiring an 80% adjustment. You must use the 75 temp ampacity due to terminal limitations, but can derate from the 90 degree. It works out using the next size up rule as you have shown as long as you use the 250 MCM, the 4/0 is too small.

Not sure if a 2 1/2 LB is sufficient. You would have to see what it is marked with and of course it won't have the combination of conductors you have. I think there is a letter from an lb manufacturer floating out there that says for combinations not printed on the lb you can compute the area of your conductors and as long as it is the same or less you're okay.
The calculation method was added to 314.28(A)(3) a few cycles ago.
 
8 space panel in meter center panel...

the included 200 A breaker on the left feeds the 8 circuit panel, which has 2 - 2 pole breakers...One is the 100A 2 pole breaker feeding
the 100 A Panel B, the other is a 20 A 2 pole breaker feeding the sprinkler pump.
Panel A is fed from the pass-through lugs ( factory installed ) at the bottom of the 8 circuit buss..

I also believe I found the perfect pvc l.b.
 

Attachments

  • 1st floor load calculation Std Method 0907 v5a 183 A.pdf
    24.8 KB · Views: 8
  • 2nd floor load calculation STANDARD CALC 0907 52 A V2 .pdf
    23.1 KB · Views: 3
  • TOTAL load calculation OPTIONAL METHOD 0907 10a 187 A.pdf
    23.8 KB · Views: 3
  • 4FYN5_2 CHECK THIS.pdf
    138.1 KB · Views: 6