Oilfield serves almost all pump loads with 480 volts delivered by utility with 480Y/277 secondary. Utility?s choice of an overhead service or from a pad mount transformer. At the service entrance in a riser, the utility wants a neutral in the riser down to an insulated neutral buss. In a pad mount transformer, a neutral is also required to go from transformer to the circuit protection panel.
The utility wants a neutral and the customer knows that a neutral will not beused at the load. Three hot legs and a grounding conductor is what will be run to the well.
My position is that a grounding conductor is all that must be connected to the utility.
What code article should I reference?
This utility has no licensing authority. Licensees are tested at the state level.
I contend that the panel must be marked and there is a risk that a load may be connected in the future that would require a neutral to operate.
The oilfield looks at the service entrance for that load only.
The utility wants a neutral and the customer knows that a neutral will not beused at the load. Three hot legs and a grounding conductor is what will be run to the well.
My position is that a grounding conductor is all that must be connected to the utility.
What code article should I reference?
This utility has no licensing authority. Licensees are tested at the state level.
I contend that the panel must be marked and there is a risk that a load may be connected in the future that would require a neutral to operate.
The oilfield looks at the service entrance for that load only.