dahualin said:
georgestolz said:
If you did, it would be a parallel conductor to the neutral. Parallel conductors are addressed in 310.4.
I don't really agree with this. The extra grounding conductor can be bonded to utility transformer enclosure and bond transformer enclosure to neutral. If it is in this situation, grounding conductor cannot bond with neutral conductor at service disconnect.
Unfortunately, 250.24(B) does not allow us that option. A main bonding jumper is required to be installed in every service; there are no exceptions for a service supplied with an EGC run with the service conductors.
There has been talk about sending a proposal their way for just such a circumstance, but there has not been any such action to date, that I'm aware of.
dahualin said:
The neutral conductor sometimes has unbalanced current. If the grounding system doesn't bond correctly, it is very likely get objectionable current run in grounding system that is very dangerous. Because all exposed conduits and other metal enclosure can be the path to person who touches those exposed metal and got shocked.
What you've written confuses me, particularly what I've underlined. A neutral conductor always carries unbalanced current. If the
neutral conductor is not securely terminated and suddenly has a high resistance or opens, then the unbalanced neutral current will begin making use of higher-resistance paths that normally carry minimal current (ie conduit, through people, through the earth, to the utility grounding electrode system(s), to the source).
A grounding electrode system will likely not bring the voltage down much in an open neutral scenario, it would depend on the particulars.
dahualin said:
The best bonding point is the power source (Service utility transformer, Separately derived system) and the second best bonding point is the service disconnent.
Theoretically, why?
In the real world, has this ever been done? I've never seen an EGC with service conductors.
Perhaps you are grouping SDSs and services in your post - would it be all right with you to focus solely on services for now, and perhaps return to SDSs later?