It would seem that the service calculations section in the NEC is somehow useless to the utility company.
every single job we do, requires that we do service calculations per NEC to justify our selection of the service equipments. The AHJ, and in most cases, it is the agency granting plan approvals, require that we comply with NEC.
On the other hand, the utility company has no interest in our calculations, because they size their transformers, or their service entrance conductors according to their rules, which in most cases, has a much lower ampacity than the NEC would require.
In my opinion, the NEC should have provisions for such calculations, and the AHJ, should accept the load calculations presented by the utilities company. Furthermore, the AHJ should not require service calculations to be part of their approval if the utility company can "do their own thing" on the service side
I would agree that if there was a single building and we're trying to sub-feed it from the main service equipments, then we can use these calculations in the NEC. Other than that, why even bother with the service equipment sizing and service calculations if the utility company is going to determine the service feeder conductors by their own demand factors. Thus, we should wait to see what is the entrance conductors, or find out what the utility's company transformer, then, size the main service equipments according to that.
every single job we do, requires that we do service calculations per NEC to justify our selection of the service equipments. The AHJ, and in most cases, it is the agency granting plan approvals, require that we comply with NEC.
On the other hand, the utility company has no interest in our calculations, because they size their transformers, or their service entrance conductors according to their rules, which in most cases, has a much lower ampacity than the NEC would require.
In my opinion, the NEC should have provisions for such calculations, and the AHJ, should accept the load calculations presented by the utilities company. Furthermore, the AHJ should not require service calculations to be part of their approval if the utility company can "do their own thing" on the service side
I would agree that if there was a single building and we're trying to sub-feed it from the main service equipments, then we can use these calculations in the NEC. Other than that, why even bother with the service equipment sizing and service calculations if the utility company is going to determine the service feeder conductors by their own demand factors. Thus, we should wait to see what is the entrance conductors, or find out what the utility's company transformer, then, size the main service equipments according to that.