cmdr_striker
Member
- Location
- Nipomo, California
- Occupation
- Mechanical Engineer
I have recently had issues with my utility creating a high ground potential on my neutral and thus ground circuits. Service is fed from an overhead 2-phase 15 kva transformer directly to the main which is properly bonded and grounded. There is a sustained 20-25 vac potential between any grounds on the property and earth even with the utility main breaker open. This can also carry a few milliamp current if connected to a independent grounding rod.
Utility has replaced the transformer and tested the wire run from the transformer to the service meter. L1 and L2 to neutral are balanced voltage even under load testing. It is simply that the service neutral/ground is at an elevated potential compared to earth ground. This can under extreme conditions result in very small shocks even with all breakers open which seems dangerous in the extreme.
With the main breaker open if the utility neutral is removed this potential and any current flow disappears. This is obviously a utility issue right? How can I convince them of this? What is a plausible explanation?
Overhead service is two-wire, both hot and this house is at the very end of a long line.
Thanks all.
Utility has replaced the transformer and tested the wire run from the transformer to the service meter. L1 and L2 to neutral are balanced voltage even under load testing. It is simply that the service neutral/ground is at an elevated potential compared to earth ground. This can under extreme conditions result in very small shocks even with all breakers open which seems dangerous in the extreme.
With the main breaker open if the utility neutral is removed this potential and any current flow disappears. This is obviously a utility issue right? How can I convince them of this? What is a plausible explanation?
Overhead service is two-wire, both hot and this house is at the very end of a long line.
Thanks all.