Hello,
I’m working on a project with a 34.5 kV three-phase distribution system, but the cutout fuses being installed are 25 kV rated (200A). It seems as though there are many different opinions about whether or not this is an acceptable application.
Obviously, the line-to-ground voltage in a 34.5kV system is around 19.9 kV. Understanding that a single fuse cutout is installed for each phase, the equipment appears to be properly rated. I've been informed by other professionals that this is a standard practice for utilities. However, some engineers argue that the cutout should be rated for 34.5 kV (phase-to-phase voltage).
In case it is helpful, the specific project being worked on is in rural Texas. I've done some digging in the RUS Bulletins for guidance (links below), but they don't specify anything that would clarify this specific situation. I'm also aware of instances like this for other equipment such as insulators.
RUS Bulletin 5-4
RUS Bulletin 1728F-803
Does anyone know of RUS standards or industry guidelines (like NESC or IEEE) that specify the correct fuse voltage rating for this scenario?
Depending on whether or not there are industry guidelines, Is is possible that the utility would be allowed to follow a different set of standards when compared to commercial/industrial installations?
I’m working on a project with a 34.5 kV three-phase distribution system, but the cutout fuses being installed are 25 kV rated (200A). It seems as though there are many different opinions about whether or not this is an acceptable application.
Obviously, the line-to-ground voltage in a 34.5kV system is around 19.9 kV. Understanding that a single fuse cutout is installed for each phase, the equipment appears to be properly rated. I've been informed by other professionals that this is a standard practice for utilities. However, some engineers argue that the cutout should be rated for 34.5 kV (phase-to-phase voltage).
In case it is helpful, the specific project being worked on is in rural Texas. I've done some digging in the RUS Bulletins for guidance (links below), but they don't specify anything that would clarify this specific situation. I'm also aware of instances like this for other equipment such as insulators.
RUS Bulletin 5-4
RUS Bulletin 1728F-803
Does anyone know of RUS standards or industry guidelines (like NESC or IEEE) that specify the correct fuse voltage rating for this scenario?
Depending on whether or not there are industry guidelines, Is is possible that the utility would be allowed to follow a different set of standards when compared to commercial/industrial installations?