Ah, Ok. What for?
Ah, Ok. What for?
Looks like a std distribution cap wired line-to-ground through a fused cutout. Since the picture seems to show a 2-phase supply to some load, perhaps the phase with the cap has much heavier load on it. Otherwise, I would've expected to see two caps instead of one.
Power Factor Correction on the line. Not necessarily associated with low PF customer loads.
I don't see a system neutral. Maybe the arrester on the far side is connected to a cutout we cant see and two hot phases go to the capacitor. I have done this with 14.4kV Delta. Around here a static capacitor will usually be connected in the summer and open in the winter. All about air conditioning load.
My impression was that for distribution lines the inductive reactance of the lines themselves contributes to a noticeable power factor effect, but I may be totally mistaken.Interesting, could you elaborate? Would that be because the accumulated effects of many small transformers?
This line is 2 phases of 4800 delta.
It is serving small services - poor power factor is not penalized with those customers, but still exists. POCO places correction where they feel is needed in their distribution, and may even switch it out of the circuit at different times of the year when power factor changes because the general loads have changed (like when air conditioning season ends).This is in a rural area, just scattered houses, middle of nowhere. Would a PF cap be typical for this kind of line and load?
My impression was that for distribution lines the inductive reactance of the lines themselves contributes to a noticeable power factor effect, but I may be totally mistaken.
It is serving small services - poor power factor is not penalized with those customers, but still exists. POCO places correction where they feel is needed in their distribution, and may even switch it out of the circuit at different times of the year when power factor changes because the general loads have changed (like when air conditioning season ends).
Today, 01:16 AMGoldDigger
My impression was that for distribution lines the inductive reactance of the lines themselves contributes to a noticeable power factor effect, but I may be totally mistaken.
Interesting, could you elaborate? Would that be because the accumulated effects of many small transformers?
This line is 2 phases of 4800 delta.
Where is the neutral? It should be above the telephone line.
They use caps like that to boost the line voltages on long distance runs. The fact that they only ran two lines indicates it's likely a long run from the nearest substation, meaning they save money on the wire and use an open delta for any three phase loads they encounter on that line.
How does a cap boost voltage? Or do you mean indirectly by improving power factor and lowering losses?