My local utility very actively diversifies connected load calculations. I understand that not everything will be turned on at the same time and that NEC requires to include safety margins.
However, in my most recent project, my calculated connected load was right at 1800 amps with 208/120v secondary. This load was calculated carefully to make sure no duplication in heating/air conditioning loads were included. The utility is offering to install 3 50kVA overhead transformers instead of an appropriately sized pad-mount. They diversified the load down to 139kVA from almost 650kVA.
How can I dispute their installation of 3 50kVA transformers for this?
Secondly, my NEC requirements have 5 parallel sets of 600kcmil conductors for the service. The utility will be providing 2 parallel sets of 500kcmil from their OH bank. How do I connect the two? I decided on a tap box. Any other ideas?
The service at this point will be OH transformer with riser down to CT/VT & meter instead of OH line with riser down to pad-mount transformer to CT/VT.
However, in my most recent project, my calculated connected load was right at 1800 amps with 208/120v secondary. This load was calculated carefully to make sure no duplication in heating/air conditioning loads were included. The utility is offering to install 3 50kVA overhead transformers instead of an appropriately sized pad-mount. They diversified the load down to 139kVA from almost 650kVA.
How can I dispute their installation of 3 50kVA transformers for this?
Secondly, my NEC requirements have 5 parallel sets of 600kcmil conductors for the service. The utility will be providing 2 parallel sets of 500kcmil from their OH bank. How do I connect the two? I decided on a tap box. Any other ideas?
The service at this point will be OH transformer with riser down to CT/VT & meter instead of OH line with riser down to pad-mount transformer to CT/VT.