Recently, we have been getting available fault current from the utility in multiple forms where in the past we had just been told the worst case. Now, we are getting data as follows on the primary bushings of a 208 3-phase pole mounted banks:
3-phase fault current: 3466A
phase to ground fault current: 3200A
positive sequence (X/R) = 2.71
zero sequence (X/R) = 2.9
They also indicated the bank will be 3 25KVA xfmrs with 12.47kV primary. The impedance for 1 transformer falls within 1.75% to 2.02% with an average of 1.88% for each transformer in the bank.
Based on all this data, I am trying to determine the secondary available fault current for the panel's AIC rating but not sure what data to use to figure the primary available fault. The program we use only has data entry for the primary available fault current, transformer KVA rating, % impedance.