We received an emergency over the weekend for a reported partial power outage to a commercial property. Here is a little background of the electrical service.
120/208v 3ph 4w. Two Main disconnects, each rated at 1200amp. Here is the problem, indeed there was a partial power outage, loss of the B ph from the utility. It was a blown fuse in the utility transformer. It blew their fuse again when they replaced it. They tested the transformer and the conductors feeding the building, no issues. They turned the mains off and it would hold.
Through some very careful troubleshooting, we narrowed it down to two very suspect branch circuits for outdoor lighting. The mains and distribution breakers are all set at their minimum trip settings or just above the minimum. This circuit(s) bypassed every overcurrent protective device without tripping one of them. So it did not trip the branch circuit breaker, main breaker in the panel, breaker that feeds the panel and the main breaker. How is this possible?
I've seen similar situations where the main opened instead of the branch circuit due to a severe short circuit of a motor, but the utility fuse, that's new.
Any input would be greatlyappreciated.
Thanks in advance,
120/208v 3ph 4w. Two Main disconnects, each rated at 1200amp. Here is the problem, indeed there was a partial power outage, loss of the B ph from the utility. It was a blown fuse in the utility transformer. It blew their fuse again when they replaced it. They tested the transformer and the conductors feeding the building, no issues. They turned the mains off and it would hold.
Through some very careful troubleshooting, we narrowed it down to two very suspect branch circuits for outdoor lighting. The mains and distribution breakers are all set at their minimum trip settings or just above the minimum. This circuit(s) bypassed every overcurrent protective device without tripping one of them. So it did not trip the branch circuit breaker, main breaker in the panel, breaker that feeds the panel and the main breaker. How is this possible?
I've seen similar situations where the main opened instead of the branch circuit due to a severe short circuit of a motor, but the utility fuse, that's new.
Any input would be greatlyappreciated.
Thanks in advance,