I know this may vary from areas, but are utility gas meters typically have a classification near and around them?
I’ve read some places on the web for a space of 3ft of space from utility gas meter to electrical meter.typically not
That’s a utility or gas company requirement. It’s not a set in stone code.I’ve read some places on the web for a space of 3ft of space from utility gas meter to electrical meter.
But I’ve seen an a/c unit with a disconnect right next to one and that made me wonder if there’s any difference there.
Urban legend.As I recall can threaded pipe connections even give you a classification. I always thought it had to be flanges.
Heard that!Urban legend.
but is a utility meter a source of ignition?The National Fuel Gas Code, NFPA 54 requires no ignition sources within 3-feet but does not use the word “classified “.
Sent from my iPhone using Tapatalk
Well, it should only arc and sparks when things go wrong...Would a disconnect be considered an ignition source I wonder? Arcing and sparking
Good pointI always figured that 3’ was working space, for either utility.
How so? Any disconnect or switch under load will produce an arc under normal conditions. That can be a potential ignition point?Well, it should only arc and sparks when things go wrong...