what is the purpose of these cables tied between phases and ground?
To make the conductors safe for working on.
In one of the areas we service the utility distributes at 39KV and will not work it hot, they shut it down and ground it out.
most likley. Utiity company will not take any chances on back-feed anymore in my area also. It only takes one person with a generator or PV that has a illegal set-up that can kill an innocent Lineman. What is strange is that they rely on tying those gounds to the Guy wire support stakes. I did not realize those stakes could handle a fault.So, the lines were dead when i took this picture? I figured those were insulators on the end of that cable.
I say they are lightning arrestors, too. We have them around here, too.iwire, if you look closely, I think they look like the surge suppressors our poco has been using the past couple of years, They seem to be a basic arc gap type. Usually when they use the grounds, it has a tag hanging off of it saying "grounded"
Not the stake, the top end. They're solidly bonded to the neutral on the pole.What is strange is that they rely on tying those gounds to the Guy wire support stakes. I did not realize those stakes could handle a fault.
"Miyagi have hope for you!"Thanks, I learned something new.
HUH neutral on the pole!Not the stake, the top end. They're solidly bonded to the neutral on the pole.
And I did see the Lineman ground to the Guywire stake.
What if you have no nuetral but three phase conductors.
I thought they were grounds as well. Thanks from me as well.
They are lightning arrestors. Alabama Power and Georgia power use them. At least that is what a lineman in Demorest Georgia told me the last time I took my daughter back to College.