Utility-interactive inverter 690.64 Point of Connection

Status
Not open for further replies.

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Can a supply side connection be made on the line side of a panel main breaker if the lugs allow multiple wires?
My understanding is yes but only if the main breaker on the panel is the service disconnect.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
While the code may permit this, you need to check with your utility. Ours requires that you have disconnect outside next to the meter for any utility interactive inverter connections. This is required even when the inverter output is connected on the load side of the service disconnect.
 