The 43.2 kW unit is three of the 14.4kW units ganged-up on a common input/output wiring box. The 33.3kW and 100kW units work in an analogous manner to this, for the 277/480V grid. These are all grid-tie only inverters, and therefore either need to be connected to the utility grid, or connected to some other grid-forming source. Such as a system of generators that is large enough to accept the inverter source, or has a system to control the inverters. Or a battery-backup inverter system.
Grid-tie, grid-interactive, utility interactive are all terms that mean the same thing. It means that the inverter's power source is subordinate to another source that establishes the grid. The inverter looks for a grid within the voltage and frequency tolerance of a "healthy grid". It will then produce a synchronized voltage waveform that is slightly higher in amplitude in order to "push" its current onto that grid. If the grid ceases to be within the voltage and frequency tolerance programmed in to the inverter's settings, the inverter will disconnect and cease operation.
The manual will describe it in more detail. Unless otherwise specified to be grid forming/batttery backup, inverters are grid interactive.