I'm not sure where to begin on this story, this is a lot of information so bear with me and please let me know your thoughts.
8 months ago I started work on a pet hospital addition. The project involved reworking the main electrical service on the building. Electrical one-line attached for reference.
Before redesign, we meet with the utility contacts to establish what the new service will look like and eventually send a load sheet with our new loads shown (pretty standard for most utilities). For this project I followed the same procedure and sent the utility contact the new design as well as the entire electrical drawing set for reference.
Well 8 months later, after the install and after the utility contact even approved the design (also AHJ approved design as well), I get an email from the contractor saying that the utility came back saying the service is not in compliance with their standards.
For reference, our design involved a 120/240V single phase service with a 600 amp CT cabinet that then fed over to a wireway with fusible disconnects. On the wireway we had three disconnects, one 300 amp switch, one 400 amp switch, and one 200 amp switch. The main service feeder was sized for the demand load which was about 500 amps.
Below is the exact message that I received from the utility:
"Our concern is with the utility service manual which states that single phase 120V/240V services are limited to 800A maximum. You have 900A worth of disconnects, though current is much less, it still poses a risk that your load could one day exceed our rated maximum."
This design is seen everywhere and I'm not sure how the utility can ignore our NEC demand load calculations, but they seem to be making up rules on the fly...
Again, this design is NEC compliant per the code sections listed below:
Per NEC section 230.71 (Maximum Number of Disconnects)
There shall be not more than six sets of disconnects per service grouped in any location. We provided three disconnect switches.
Per NEC section 230.80 (Combined Rating of Disconnects)
This section says, "It is possible for the total of the six overcurrent devices to be greater than the rating of the service-entrance conductors. However, the size of the service entrance conductors is required to be adequate for the computed load only, and each individual service disconnecting means is required to be large enough for the individual load it supplies. See the commentary following 230.90(A), exception No. 3.
Per NEC section 230.90(A) exception No. 3
Two to six circuit breakers or sets of fuses shall be permitted as the overcurrent device to provide the over-load protection. The sum of the ratings of the circuit breakers or fuses shall be permitted to exceed the ampacity of the service conductors, provided the calculated load does not exceed the ampacity of the service conductors.
One final point, but the feeder from the utility transformer secondary to the service entrance is customer provided so I'm not sure why they are so concerned with our feeders.
I've worked with this utility hundreds of times and this is the first time I've ever dealt with a problem like this. Should I give up trying to argue my point with the utility even though I literally sent my utility contact all the info 8 months ago which he approved at one point. I'm at a loss on this one
8 months ago I started work on a pet hospital addition. The project involved reworking the main electrical service on the building. Electrical one-line attached for reference.
Before redesign, we meet with the utility contacts to establish what the new service will look like and eventually send a load sheet with our new loads shown (pretty standard for most utilities). For this project I followed the same procedure and sent the utility contact the new design as well as the entire electrical drawing set for reference.
Well 8 months later, after the install and after the utility contact even approved the design (also AHJ approved design as well), I get an email from the contractor saying that the utility came back saying the service is not in compliance with their standards.
For reference, our design involved a 120/240V single phase service with a 600 amp CT cabinet that then fed over to a wireway with fusible disconnects. On the wireway we had three disconnects, one 300 amp switch, one 400 amp switch, and one 200 amp switch. The main service feeder was sized for the demand load which was about 500 amps.
Below is the exact message that I received from the utility:
"Our concern is with the utility service manual which states that single phase 120V/240V services are limited to 800A maximum. You have 900A worth of disconnects, though current is much less, it still poses a risk that your load could one day exceed our rated maximum."
This design is seen everywhere and I'm not sure how the utility can ignore our NEC demand load calculations, but they seem to be making up rules on the fly...
Again, this design is NEC compliant per the code sections listed below:
Per NEC section 230.71 (Maximum Number of Disconnects)
There shall be not more than six sets of disconnects per service grouped in any location. We provided three disconnect switches.
Per NEC section 230.80 (Combined Rating of Disconnects)
This section says, "It is possible for the total of the six overcurrent devices to be greater than the rating of the service-entrance conductors. However, the size of the service entrance conductors is required to be adequate for the computed load only, and each individual service disconnecting means is required to be large enough for the individual load it supplies. See the commentary following 230.90(A), exception No. 3.
Per NEC section 230.90(A) exception No. 3
Two to six circuit breakers or sets of fuses shall be permitted as the overcurrent device to provide the over-load protection. The sum of the ratings of the circuit breakers or fuses shall be permitted to exceed the ampacity of the service conductors, provided the calculated load does not exceed the ampacity of the service conductors.
One final point, but the feeder from the utility transformer secondary to the service entrance is customer provided so I'm not sure why they are so concerned with our feeders.
I've worked with this utility hundreds of times and this is the first time I've ever dealt with a problem like this. Should I give up trying to argue my point with the utility even though I literally sent my utility contact all the info 8 months ago which he approved at one point. I'm at a loss on this one