Existing building being renovated. Existing utility transformer and (I believe) utility-owned service conductors. Thus, the utility-owner transition would be the lugs of the main breaker on the main service panel. That panel is rated 800 amps, and the main breaker is 800 amps. Let us assume a calculated load of 600 amps.
My information is that the service conductors are (2) sets of 500 MCM Aluminum. That has an ampacity of 620. Under NEC rules, you can?t protect a 620 amp conductor set with an 800 amp breaker (i.e., next higher standard size is 700). Furthermore, you can?t take advantage of the ?next higher standard rating? rule in 240.4(B) for transformer secondary conductors. So the breaker has to be 600 or lower.
Here?s the question: Is this something I can ignore, given that the service conductors belong to the utility? Or is it the responsibility of the owner (whose interests are to be safeguarded by the design engineer ? myself) to ensure that the main breaker is capable of protecting the service conductors in accordance with NEC rules? Specifically, should I call for a design change to replace or reset the breaker to a maximum trip of 600 amps?
My information is that the service conductors are (2) sets of 500 MCM Aluminum. That has an ampacity of 620. Under NEC rules, you can?t protect a 620 amp conductor set with an 800 amp breaker (i.e., next higher standard size is 700). Furthermore, you can?t take advantage of the ?next higher standard rating? rule in 240.4(B) for transformer secondary conductors. So the breaker has to be 600 or lower.
Here?s the question: Is this something I can ignore, given that the service conductors belong to the utility? Or is it the responsibility of the owner (whose interests are to be safeguarded by the design engineer ? myself) to ensure that the main breaker is capable of protecting the service conductors in accordance with NEC rules? Specifically, should I call for a design change to replace or reset the breaker to a maximum trip of 600 amps?