netaguy
- Providence, RI
Ok, I have seen this 3 times in one week so now I am questioning this.
I was called by a mechanical contractor to look into supplying 1000A of temporary power to a roll up chiller unit because an old gas absorber failed at a large department store.
The customer says I have a 4000A service, plenty of availibility. Sure enough, 4000A 480/277V switchboard, 4000A main, 1033 amps on the IQ meter.
In the parking lot sits the utility owned oil transformer on a pad. 1500KVA label right on the front of it. Sorry, not going to happen anytime soon. I tell them apparently the utility company knows that this store would never need a 4000A service and installed a 1500KVA.
Now, last weekend during a utility outage at an office building about 15 years old I see something typical. The incoming at the switchboard there are (10) sets of 4 - 600MCM Cu. The utility company owned oil transformer on the pad is opened and there are (6) sets of 500MCM AL. Once again, 1500KVA 13.8kV to 480/277V rated transformer.
In between there is a pad mount collector box, (never seen this before, but I hear it is common in this area) sort of an electric demarc. The (10) sets done by original contractor out to collector, the (6) sets to transformer done by utility.
Now I am curious. I check the main 4000A breaker and it is set at 100%.
My question is how are the transformer secondary conductors protected properly? They are in PVC underground duct bank to the switchboard but how are they protected if the main breaker is set over 2X the transformer output rating?
BTW - this is typical on a building further up the street with a 1000KVA transformer and a 3000A main breaker/switchboard.
Thanks for your help.