There will be a 2000kVA (12.47-480/277) utility owned transformer located just outside of a building. The user owned service gear will also be located outside of the building and very close to the utility transformer.
The utility will bond the neutral to ground within the transformer enclosure. The NEC requires that the neutral be bonded to ground in the service gear.
There are several questions associated with this arrangement:
1. This arrangement does not create "objectionable" ground current and violate NEC 250.30(A)(1) Exception #2 if the equipment is located on separate concrete pads. However it seems to violate 250.50 which states that the grounding electrode system needs to be bonded together.
2. Since the utility owns the transformer is it Ok to put blinders on and let them do what ever they want. Couldn't this arrangement result in unbalance neutral current flows over ground grid which could falsely trip ground fault devices?
3. What if the equipment were on the same concrete pad.
All comments appreciated.
The utility will bond the neutral to ground within the transformer enclosure. The NEC requires that the neutral be bonded to ground in the service gear.
There are several questions associated with this arrangement:
1. This arrangement does not create "objectionable" ground current and violate NEC 250.30(A)(1) Exception #2 if the equipment is located on separate concrete pads. However it seems to violate 250.50 which states that the grounding electrode system needs to be bonded together.
2. Since the utility owns the transformer is it Ok to put blinders on and let them do what ever they want. Couldn't this arrangement result in unbalance neutral current flows over ground grid which could falsely trip ground fault devices?
3. What if the equipment were on the same concrete pad.
All comments appreciated.