I was provided this Utility Drawing by my local utility. I'm having the pole transformer moved to another pole and running underground to a new disconnect/meter on the side of the home during a re-truss of the home which requires removal of the existing overhead.
The utility requires conduit due to the rocky soil (confirmed rocky during trenching, terrible). This is creating issues for me in specifying a proper conductor type for the run. It's 4/0-4/0-2/0 Al but the issue here is my loop from the weatherhead to the pole transformer. Everyone has suggested URD (specifically Southwire Sweetbriar 55418406) but the exposed loop concerns me. I can't find anything stating this is UV rated and the jacketing is cross linked polyethylene. That's the same material as PEX which is certainly not rated for UV exposure.
Anybody had a similar application? What did you ultimately go with? This is a 2" conduit run of about 160' with two vertical 90s, one horizontal 90 and two horizontal 45s.
The utility requires conduit due to the rocky soil (confirmed rocky during trenching, terrible). This is creating issues for me in specifying a proper conductor type for the run. It's 4/0-4/0-2/0 Al but the issue here is my loop from the weatherhead to the pole transformer. Everyone has suggested URD (specifically Southwire Sweetbriar 55418406) but the exposed loop concerns me. I can't find anything stating this is UV rated and the jacketing is cross linked polyethylene. That's the same material as PEX which is certainly not rated for UV exposure.
Anybody had a similar application? What did you ultimately go with? This is a 2" conduit run of about 160' with two vertical 90s, one horizontal 90 and two horizontal 45s.