divemaster5734
Member
- Location
- Seattle
I'm a 01 Master in Washington State. We got a call that a small condo complex of Air BnB rentals had guests that were getting shocked when entering or exiting the hot tub.
After checking all the basics, make up, terminating, bonding, operational condition of 50A 2P GFCI spa disconnect, etc, and verifying there were no transient voltages present inside any of the residences I then addressed the 8 gang meter section.
The bonding was good, they did not bond the neutral at the meters, making the electrical point of attachment bond at each unit instead.
There was the typical oxidation present on the ground busses, which I removed and observed the machine screw threads were shiny with screws removed, indicating there was still a good electrical connection, and even though the unit had been mounted around mid to late 70's, all AL conductors had generous amount of Deox, but I wire brushed all the paint from the entire buss contact area, and applied deox to all surfaces.
I then stuck one lead from my Fluke T-6 1000 in the acorn of the first ground rod, the other lead into the dirt a foot away, and got a 56 VAC reading.
The meter bank is fed with 2 x 4/0 USE in parallel that is direct buried.
I then used a Greenlee Pulsar PE2000 and located a 19" section of B phase with the insulation blown out.
I replaced that section, retested all phases and both neutrals, getting a perfect reading on the Pulsar meter.
Once all that was done I am still getting a voltage from the ground rod to the earth.
It increases by about 14VAC with each main breaker that is energized.
The utility crew was not very forthcoming about their side of the distribution and it took a little "reading between the lines" to discover a cover-up.
Once I exposed it, they then admitted they had a primary feeder short out, which blew a transformer, and sent a 7200 VAC surge through their secondary, blowing a Comcast box and left a 8" carbon arc across the ground buss inside the cabinet.
They replaced that transformer, which fed the property next door.
On the other side is a park, which also has a city duplex lift station, fed by another transformer, which they also replaced, but claimed it was only replaced because it had a broken latch.
I seriously doubt that was the only issue. It's a 150KVA pad mounted one, and they had to get a new vault cover.
The work was done over a weekend.
I know there is only one vendor for the utility vaults, they are not open on weekends, and if they had to open up on a Saturday or Sunday they make it hurt.
Those vault covers weigh over 4000lbs, I know because I have set several 4' x 8' underground vaults.
I noticed it had a new sticker from the vault company, so it could not have been sitting around in the utility's back yard.
The way that utility works there had to have been at least 20 people from two different divisions, all on double time.
They spent at least $60,000 to replace that transformer instead of spending $500 for an entire latching rod and handle system.
There is another small transformer that feeds my customer between the two they changed out, and they did not touch that one.
I did not take pictures of the ground voltage, but did take some of the blown out wire.
I've seen 6" to 8" blow outs, but never one 19" long.
The utility swears there is nothing wrong with that transformer, but I think it's to avoid liability.
I'm at the end of knowledge area, the ground is dry, and I know funny stuff happens when there's not enough moisture in the earth to help ground paths, but I'm from an area that isn't far from a rain forest, and we haven't experienced dry earth issues like this in the 20 years I've been in this area.
I'm hoping someone in a more arid climate might have some insights.
Thanks in advance
After checking all the basics, make up, terminating, bonding, operational condition of 50A 2P GFCI spa disconnect, etc, and verifying there were no transient voltages present inside any of the residences I then addressed the 8 gang meter section.
The bonding was good, they did not bond the neutral at the meters, making the electrical point of attachment bond at each unit instead.
There was the typical oxidation present on the ground busses, which I removed and observed the machine screw threads were shiny with screws removed, indicating there was still a good electrical connection, and even though the unit had been mounted around mid to late 70's, all AL conductors had generous amount of Deox, but I wire brushed all the paint from the entire buss contact area, and applied deox to all surfaces.
I then stuck one lead from my Fluke T-6 1000 in the acorn of the first ground rod, the other lead into the dirt a foot away, and got a 56 VAC reading.
The meter bank is fed with 2 x 4/0 USE in parallel that is direct buried.
I then used a Greenlee Pulsar PE2000 and located a 19" section of B phase with the insulation blown out.
I replaced that section, retested all phases and both neutrals, getting a perfect reading on the Pulsar meter.
Once all that was done I am still getting a voltage from the ground rod to the earth.
It increases by about 14VAC with each main breaker that is energized.
The utility crew was not very forthcoming about their side of the distribution and it took a little "reading between the lines" to discover a cover-up.
Once I exposed it, they then admitted they had a primary feeder short out, which blew a transformer, and sent a 7200 VAC surge through their secondary, blowing a Comcast box and left a 8" carbon arc across the ground buss inside the cabinet.
They replaced that transformer, which fed the property next door.
On the other side is a park, which also has a city duplex lift station, fed by another transformer, which they also replaced, but claimed it was only replaced because it had a broken latch.
I seriously doubt that was the only issue. It's a 150KVA pad mounted one, and they had to get a new vault cover.
The work was done over a weekend.
I know there is only one vendor for the utility vaults, they are not open on weekends, and if they had to open up on a Saturday or Sunday they make it hurt.
Those vault covers weigh over 4000lbs, I know because I have set several 4' x 8' underground vaults.
I noticed it had a new sticker from the vault company, so it could not have been sitting around in the utility's back yard.
The way that utility works there had to have been at least 20 people from two different divisions, all on double time.
They spent at least $60,000 to replace that transformer instead of spending $500 for an entire latching rod and handle system.
There is another small transformer that feeds my customer between the two they changed out, and they did not touch that one.
I did not take pictures of the ground voltage, but did take some of the blown out wire.
I've seen 6" to 8" blow outs, but never one 19" long.
The utility swears there is nothing wrong with that transformer, but I think it's to avoid liability.
I'm at the end of knowledge area, the ground is dry, and I know funny stuff happens when there's not enough moisture in the earth to help ground paths, but I'm from an area that isn't far from a rain forest, and we haven't experienced dry earth issues like this in the 20 years I've been in this area.
I'm hoping someone in a more arid climate might have some insights.
Thanks in advance