My Pump Station Load is listed below and the Main Utility Transformer Supplying this load is 150KVA. From adding up all the current draw. The Pump Station Load is greater than the Secondary Transformer FLA. The Utility Engineer informed although the FLA has been exceeded the Operational Limits of the transformer has not. Can someone explain why this is ok? Also what NEC standard section to reference as well?
Pump Station Load
50HP, Current Draw = 65
15HP, Current Draw = 21
25HP, Current Draw = 34
2HP, Current Draw = 3.4
Total = 274.4
Utility Transformer
Pri Volt: 16.34 KV, Secondary Volt: 480VAC
Rating: 150KVA, Secondary FLA: 180 FLA
Pump Station Load
Total = 274.4
Utility Transformer