I have utility transformer outside building with service conductors going into 1200A tap box which then has four service disconnects.
The utility transformer has ground ring with ground rods. The four service disconnects each have grounding electrode conductor going to bus bar. From bus bar there is grounding electrode conductors going to steel, water pipe, triad ground rods.
What I also noticed is their is bonding jumper from triad ground rods to the utility transformer ground ring with ground rods.
I understand that all grounding electrodes need to be bonded at the building but does the utility transformer ground ring with ground rods should also be bonded?
The utility transformer has ground ring with ground rods. The four service disconnects each have grounding electrode conductor going to bus bar. From bus bar there is grounding electrode conductors going to steel, water pipe, triad ground rods.
What I also noticed is their is bonding jumper from triad ground rods to the utility transformer ground ring with ground rods.
I understand that all grounding electrodes need to be bonded at the building but does the utility transformer ground ring with ground rods should also be bonded?