Gentlemen (and ladies!) -
I recently received this comment from an engineer on a set of drawings and would like some input (the transformer referenced in his comment is a customer-owned utility transformer):
Recommend adding note to ensure transformer ground/neutral NOT bonded at transformer (a lot of the time transformers come from the factory bonded) where this is done in the service disconnect.
Somebody please tell me that I am reading his comment wrong and he is NOT telling me to do the opposite of 2020 NEC 250.24(A)(2)?!?!
Thanks!