Scenario 1:
Incoming Utility through a distribution transformer,(MV to LV, Wye, 4Wire), then to a 4Pole breaker at a Paralleling Switchgear.Two generators (G1 and G2) connected through 3Pole breakers on the generators and in the Paralleling Switchgear.
The generators have an integral 3Pole Breaker with power monitoring to over voltage, under voltage, ground fault, etc…
The AHJ adamantly requires neutral/grounding bond at the transformer secondary side.
When utility power is out, the Paralleling Switchgear starts generator 1 , opens the utility 4Pole breaker, closes Generator 1 breaker, and power is provided via Generator 1.
Issue 1: The opening of the utility 4Pole breaker disconnects the neutral/grounding bond from the circuit. The neutral is now floating. If maintenance or testing of generator 2 were needed, even if generator 2 3Pole paralleling switchgear breaker was locked and tagged out, the crew would be working in and around a neutral under live load. If they accidentally create a solid path from neutral to grounding (generator frame, etc...), there is no ground fault protection and a shock hazard exists.
True or False?
Incoming Utility through a distribution transformer,(MV to LV, Wye, 4Wire), then to a 4Pole breaker at a Paralleling Switchgear.Two generators (G1 and G2) connected through 3Pole breakers on the generators and in the Paralleling Switchgear.
The generators have an integral 3Pole Breaker with power monitoring to over voltage, under voltage, ground fault, etc…
The AHJ adamantly requires neutral/grounding bond at the transformer secondary side.
When utility power is out, the Paralleling Switchgear starts generator 1 , opens the utility 4Pole breaker, closes Generator 1 breaker, and power is provided via Generator 1.
Issue 1: The opening of the utility 4Pole breaker disconnects the neutral/grounding bond from the circuit. The neutral is now floating. If maintenance or testing of generator 2 were needed, even if generator 2 3Pole paralleling switchgear breaker was locked and tagged out, the crew would be working in and around a neutral under live load. If they accidentally create a solid path from neutral to grounding (generator frame, etc...), there is no ground fault protection and a shock hazard exists.
True or False?