Utility transformer secondary LTC to get 240 V from 277V

Status
Not open for further replies.

boshbosh43

New User
Location
Clermont Florida
Occupation
Electrical project engineer
Coming across an issue, we have installed a level 2 (AC) EV charger, and input AC voltage setup selected was 277V ( retrieving a phase to neutral ) from the Utility Transformer 480V. Yesterday we found that the charger is set up for 240/208 V.

I am aware that we will most likely have to install a step down transformer 277 à 240 V, but could we install a LTC ( Load Tap Changer ) on the Utility transformer secondary winding ( on one phase only) tapping that 277V to 240 V , that way we won’t have any discrepancy or making any demolition and re-work the entire installation/wiring? In such a way that it won’t violate the NEC code?
Thanks
 
LTCs that I know of move all the phases. I don't know of a LTC that could modify the voltage by more than 5%.

Modifying the service in such a way can negatively impact everything else on it.

Trying to wire the device in such a way will definitely violate the manufacturer's instructions / warranty.
 