Alfont1120
- Dighton, MA
- Electrical Project Manager/Journeyman Electrician
The local utility has a padmount 13.8 to 480V transformer at the street. Our plans show us coming out of that with 4-wire plus ground and hitting a 300A fused disconnect. From there, we hit a 225kva 480 to 208V transformer which goes to a 600A fused disco ahead of the first panel. The engineered drawing calls for a 4-wire plus ground coming out of the utility transformer but that doesn't seem right. I don't see why we'd need a neutral since we will get one out of the X0 of the 225kva. The more I think about it, even pulling a ground from the utility transformer is starting to seem off as well. Do I just pull 3 phases to the 300A disco and 3 phases and a ground from that disco to the 225kva and bond it there?